Add Mod10 to Custom Data Type Manipulator for Modbus Interface

Please add support for SquareD Mod10 custom datatype to the Modbus Interface.

Schneider Electric uses a custom datatype that uses four 16 bit registers. Each register represents an integer. Each integer is then multiplied by a factor and all results are added together.
Currently the only way I know how to read this is to create a PI modbus point for each register value, then create a calculated PI point to perform the math to add them together. All the values are in consecutive registers, so they could be read with one call to the device, if there were a built in calculation to combine them. As it is now it takes four calls to the device to get the one value. It also takes 5 PI Tags when it could only take one.

Register List for PM800 Series Power Meters
MOD10
Each register represents a value from 0-9999, these register values are then appended to one another (number of registers is dependent on size of the Mod10 value) to form a data value (first register is least significant). Mod10_Value = (Register4 * 1000000000000) + (Register3 * 100000000) + (Register2 * 10000) + (Register1)

1 vote
Sign in Sign in with OSIsoft
Signed in as (Sign out)

We’ll send you updates on this idea

TimothyVann shared this idea  ·   ·  Flag idea as inappropriate…  ·  Admin →

0 comments

Sign in Sign in with OSIsoft
Signed in as (Sign out)
Submitting...

Feedback and Knowledge Base

Posted ideas will have one of the following statuses.
Full definition of these statuses can be found on the Home Page.
No status
NEEDS MORE DISCUSSION
RESEARCHING/EVALUATING
DECLINED
PLANNED
STARTED/IN DEVELOPMENT
IN BETA
COMPLETED